</a JR Holmes Oil Company </a Shark Guard Southeast Woods and Whitetail Mayer Insurance Services LLC
Aldeer Classifieds
Remington LVSF
by extreme heights hunter. 04/24/25 11:54 AM
WTB Toyota Sequoia
by AUjerbear. 04/24/25 07:08 AM
WTB 7.5hp motor
by Jtb51b. 04/24/25 06:25 AM
16x48 aluminum boat motor and trailer
by TurkeyJoe. 04/23/25 03:56 PM
Full body mount deer
by twaldrop4. 04/22/25 03:27 PM
Serious Deer Talk
Taxidermy Story
by mathews prostaff. 04/24/25 11:32 AM
Anyone here currently doing a timber co lease?
by Lockjaw. 04/22/25 03:30 PM
Mark Buxton and Clover
by CNC. 04/17/25 08:58 PM
Kentucky Deer Hunt
by booner. 04/15/25 10:35 AM
Can’t Believe
by TDog93. 04/08/25 03:21 PM
April
S M T W T F S
1 2 3 4 5
6 7 8 9 10 11 12
13 14 15 16 17 18 19
20 21 22 23 24 25 26
27 28 29 30
Land, Leases, Hunting Clubs
Pike County HC
by Double Down. 04/23/25 07:18 PM
Looking for a club around Black Pond/Double Spring
by FreeStateHunter. 04/15/25 03:57 PM
Mobile County Lease Opportunity
by booner. 04/15/25 09:25 AM
Kansas Muzzleloader / Bow
by Letshunt. 04/14/25 01:11 PM
Looking Tuscaloosa county
by twaldrop4. 04/10/25 04:51 PM
Who's Online Now
69 registered members (jdfarm23, blade, Chiller, kyles, grundan, joe sixpack, HDS64, Buckshot77, Bread, Jtb51b, Backwards cowboy, AU coonhunter, Bmyers142, sidehitter, scrubbuck, Bustinbeards, bambam32, misfire, jchurch, booner, Skinner, Hoytdad10, GomerPyle, GHTiger10, brushwhacker, AU338MAG, BearBranch, fur_n_feathers, 7x57_Mauser, lthrstkg1, chuck216, CrappieMan, rrice0725, CatfishJunkie, crenshawco, bamafan1966, Mbrock, abolt300, Coosa1, apolloslade, Chaser357, Fl Panhandler, JohnG, DoeNut, BrentsFX4, slipperyrock, Tree Dweller, cartervj, AUjerbear, MoeBuck, Turkey_neck, kpswihart, goodman_hunter, ucmducks, Jdkprp70, StateLine, dustymac, EricS, bamaeyedoc, Driveby, coosabuckhunter, 8 invisible), 525 guests, and 0 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Page 2 of 2 1 2
Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1269935
02/19/15 05:55 AM
02/19/15 05:55 AM
Joined: Feb 2014
Posts: 3,812
Scottsboro Al
T
TravisBatey Offline
10 point
TravisBatey  Offline
10 point
T
Joined: Feb 2014
Posts: 3,812
Scottsboro Al
I wouldn't change out the contactor unless just for the heck of it. Especially if the noise stops when you turn off the breaker for the outdoor system (while leaving the air handler breaker on) with the heat "on".
In the past three days, working in the Huntsville area we have took or ran 5-10 calls a day with ice building up on fan blades from the misty rain or water dripping off of roofs, that'll definately cause some noise issues and make a fan run out of balance. If you see no ice on the fan blade and everything seems to be running smooth it's probably just due to the fact that it's past its structural balance point and running at the max that it can. When the weather pushes units to their max it's not uncommon for them to make a little more noise, especially on builder grade equipment. Also as several others stated, lack of routine maintenance can also make things a little worst in the peak seasons.
I'm a service tech at a large reputable company in Huntsville. If you need someone to come out and look at it, shoot me a pm with a ph number and I can get you some info.

Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1270391
02/19/15 12:29 PM
02/19/15 12:29 PM
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
J
JTapia Offline
8 point
JTapia  Offline
8 point
J
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
Just some observations:
*Listening to the noise on the link, it sounds very much like a bad bearing or something hitting the fan blade.
**It also kinda sounds like a chattering contactor.
***The breaker the OP said was turned off was labeled "heat". This tells me that he turned off the AHU inside which has the LV Xformer which in turn would shut down the outside unit also.
****the better test would be as Steelman noted, turn off the disconnect to the outside unit while leaving the inside AHU running. This disconnect should be located next to the outside unit. This way the contactor will stay engaged while the unit stops due to lack of power. If the noise remains, it's the contactor. if it stops it's something with the units moving parts, ie; fan, compressor or combination.


Hunt'em hard when they are hard to hunt but never, ever hardly hunt!
Re: Any HVAC Folks in Here? [Re: JTapia] #1270410
02/19/15 12:46 PM
02/19/15 12:46 PM
Joined: Jan 2015
Posts: 26
NAL
T
theguyonthecouch Offline OP
spike
theguyonthecouch  Offline OP
spike
T
Joined: Jan 2015
Posts: 26
NAL
Originally Posted by JTapia
Just some observations:
*Listening to the noise on the link, it sounds very much like a bad bearing or something hitting the fan blade.
**It also kinda sounds like a chattering contactor.
***The breaker the OP said was turned off was labeled "heat". This tells me that he turned off the AHU inside which has the LV Xformer which in turn would shut down the outside unit also.
****the better test would be as Steelman noted, turn off the disconnect to the outside unit while leaving the inside AHU running. This disconnect should be located next to the outside unit. This way the contactor will stay engaged while the unit stops due to lack of power. If the noise remains, it's the contactor. if it stops it's something with the units moving parts, ie; fan, compressor or combination.


Okay, this time, I killed the outside unit at the outside disconnect and took a video while heat was ON at the thermostat. Is that a normal sound? Its a little louder in the video. You can download the new video here: SOUND

Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1270497
02/19/15 01:57 PM
02/19/15 01:57 PM
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
J
jbatey1 Offline
Lucky Bastage
jbatey1  Offline
Lucky Bastage
J
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al

Originally Posted by theguyonthecouch
Originally Posted by JTapia
Just some observations:
*Listening to the noise on the link, it sounds very much like a bad bearing or something hitting the fan blade.
**It also kinda sounds like a chattering contactor.
***The breaker the OP said was turned off was labeled "heat". This tells me that he turned off the AHU inside which has the LV Xformer which in turn would shut down the outside unit also.
****the better test would be as Steelman noted, turn off the disconnect to the outside unit while leaving the inside AHU running. This disconnect should be located next to the outside unit. This way the contactor will stay engaged while the unit stops due to lack of power. If the noise remains, it's the contactor. if it stops it's something with the units moving parts, ie; fan, compressor or combination.


Okay, this time, I killed the outside unit at the outside disconnect and took a video while heat was ON at the thermostat. Is that a normal sound? Its a little louder in the video. You can download the new video here: SOUND


Is that the noise that you have been hearing that is concerning to you when the system is running? From what I can tell from this video the noise sounds as if its a contactor buzzing. If the noise I hear is the same noise that you recorded, if that makes sense.


The fool tells me his reasons; the wise man persuades me with my own.
Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1270520
02/19/15 02:12 PM
02/19/15 02:12 PM
Joined: Feb 2014
Posts: 3,812
Scottsboro Al
T
TravisBatey Offline
10 point
TravisBatey  Offline
10 point
T
Joined: Feb 2014
Posts: 3,812
Scottsboro Al
Yall having to enter credit card info to listen to this video? It won't let me just listen to it with out signing up.

Re: Any HVAC Folks in Here? [Re: TravisBatey] #1270552
02/19/15 02:41 PM
02/19/15 02:41 PM
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
J
jbatey1 Offline
Lucky Bastage
jbatey1  Offline
Lucky Bastage
J
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
Originally Posted by TravisBatey
Yall having to enter credit card info to listen to this video? It won't let me just listen to it with out signing up.


It pulls up another web page for me then has a download link.


The fool tells me his reasons; the wise man persuades me with my own.
Re: Any HVAC Folks in Here? [Re: jbatey1] #1270596
02/19/15 03:19 PM
02/19/15 03:19 PM
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
J
JTapia Offline
8 point
JTapia  Offline
8 point
J
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
Originally Posted by jbatey1

Originally Posted by theguyonthecouch
Originally Posted by JTapia
Just some observations:
*Listening to the noise on the link, it sounds very much like a bad bearing or something hitting the fan blade.
**It also kinda sounds like a chattering contactor.
***The breaker the OP said was turned off was labeled "heat". This tells me that he turned off the AHU inside which has the LV Xformer which in turn would shut down the outside unit also.
****the better test would be as Steelman noted, turn off the disconnect to the outside unit while leaving the inside AHU running. This disconnect should be located next to the outside unit. This way the contactor will stay engaged while the unit stops due to lack of power. If the noise remains, it's the contactor. if it stops it's something with the units moving parts, ie; fan, compressor or combination.


Okay, this time, I killed the outside unit at the outside disconnect and took a video while heat was ON at the thermostat. Is that a normal sound? Its a little louder in the video. You can download the new video here: SOUND


Is that the noise that you have been hearing that is concerning to you when the system is running? From what I can tell from this video the noise sounds as if its a contactor buzzing. If the noise I hear is the same noise that you recorded, if that makes sense.


Steelman hit it....it's the Contactor. An easy change out.

With the power to the outside unit off and the inside unit on, the contactor is the only thing outside that will have power to it being that it is low voltage controlled and low voltage comes from the xformer located and powered in the inside unit(AHU)

Last edited by JTapia; 02/19/15 03:21 PM.

Hunt'em hard when they are hard to hunt but never, ever hardly hunt!
Re: Any HVAC Folks in Here? [Re: JTapia] #1270639
02/19/15 03:47 PM
02/19/15 03:47 PM

S
steelman
Unregistered
steelman
Unregistered
S


Originally Posted by JTapia
Originally Posted by jbatey1

Originally Posted by theguyonthecouch
Originally Posted by JTapia
Just some observations:
*Listening to the noise on the link, it sounds very much like a bad bearing or something hitting the fan blade.
**It also kinda sounds like a chattering contactor.
***The breaker the OP said was turned off was labeled "heat". This tells me that he turned off the AHU inside which has the LV Xformer which in turn would shut down the outside unit also.
****the better test would be as Steelman noted, turn off the disconnect to the outside unit while leaving the inside AHU running. This disconnect should be located next to the outside unit. This way the contactor will stay engaged while the unit stops due to lack of power. If the noise remains, it's the contactor. if it stops it's something with the units moving parts, ie; fan, compressor or combination.


Okay, this time, I killed the outside unit at the outside disconnect and took a video while heat was ON at the thermostat. Is that a normal sound? Its a little louder in the video. You can download the new video here: SOUND


Is that the noise that you have been hearing that is concerning to you when the system is running? From what I can tell from this video the noise sounds as if its a contactor buzzing. If the noise I hear is the same noise that you recorded, if that makes sense.


Steelman hit it....it's the Contactor. An easy change out.

With the power to the outside unit off and the inside unit on, the contactor is the only thing outside that will have power to it being that it is low voltage controlled and low voltage comes from the xformer located and powered in the inside unit(AHU)


Don't nobody want to listen to squirrelman grin

Last edited by steelman; 02/19/15 03:48 PM.
Re: Any HVAC Folks in Here? [Re: ] #1270698
02/19/15 04:13 PM
02/19/15 04:13 PM
Joined: Jan 2015
Posts: 26
NAL
T
theguyonthecouch Offline OP
spike
theguyonthecouch  Offline OP
spike
T
Joined: Jan 2015
Posts: 26
NAL
Okay, so you guys think its worth changing out the contactor. Anything special that I need to know?

Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1270718
02/19/15 04:23 PM
02/19/15 04:23 PM
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
J
jbatey1 Offline
Lucky Bastage
jbatey1  Offline
Lucky Bastage
J
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
If you believe that the noise you hear is from the contactor buzzing, replace it. They are inexpensive.

You'll need to know if you need a 1 pole or a 2 pole contactor. They are simple to change out, just kill the breaker at the outdoor unit and the breaker for the air handler. Replace the part 1 wire at a time or label them.


The fool tells me his reasons; the wise man persuades me with my own.
Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1275764
02/24/15 07:58 AM
02/24/15 07:58 AM
Joined: Jan 2015
Posts: 26
NAL
T
theguyonthecouch Offline OP
spike
theguyonthecouch  Offline OP
spike
T
Joined: Jan 2015
Posts: 26
NAL
Okay, I changed the contactor and the noise is still there. I've looked at a few videos online and the closest thing Ive found that describes the noise is that it sounds like its constantly running in defrost mode...but with the fan on. Again, when the unit turns off, theres no noise at all. Does that make sense? Any other ideas? Thanks!

Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1275833
02/24/15 08:55 AM
02/24/15 08:55 AM
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al
J
jbatey1 Offline
Lucky Bastage
jbatey1  Offline
Lucky Bastage
J
Joined: Jan 2014
Posts: 10,573
Scottsboro, Al

Originally Posted by theguyonthecouch
Okay, I changed the contactor and the noise is still there. I've looked at a few videos online and the closest thing Ive found that describes the noise is that it sounds like its constantly running in defrost mode...but with the fan on. Again, when the unit turns off, theres no noise at all. Does that make sense? Any other ideas? Thanks!


I didn't think the contactor would help much.. I would just call a company to come look at it. A diagnostic fee should be around 50-60 bucks and then you'll have a definite answer.


The fool tells me his reasons; the wise man persuades me with my own.
Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1276859
02/24/15 10:21 PM
02/24/15 10:21 PM
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
J
JTapia Offline
8 point
JTapia  Offline
8 point
J
Joined: Sep 2013
Posts: 1,636
Florida Panhandle
Originally Posted by theguyonthecouch
Okay, I changed the contactor and the noise is still there. I've looked at a few videos online and the closest thing Ive found that describes the noise is that it sounds like its constantly running in defrost mode...but with the fan on. Again, when the unit turns off, theres no noise at all. Does that make sense? Any other ideas? Thanks!


Wait.....didn't you say that you turned the outside unit off when you recorded the 2nd recording? Was that noise coming from the outside unit with the disconnect to it turned off and ONLY the inside unit running?

With the outside unit off the only thing that can be powered will be the circuit board and the contactor. They are the only things that are Low Voltage powered and that Low Voltage power comes from the Transformer inside the inside unit.
With the outside unit off the compressor won't be pushing refrigerant thru the lines so there shouldn't be much noise coming from that.

I agree with jbatey, call a professional to come out and look at it.


Hunt'em hard when they are hard to hunt but never, ever hardly hunt!
Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1276931
02/25/15 03:07 AM
02/25/15 03:07 AM
Joined: Aug 2013
Posts: 3,533
louisiana
D
deerman24 Offline
10 point
deerman24  Offline
10 point
D
Joined: Aug 2013
Posts: 3,533
louisiana
probably heat pump and the noise is normal

Re: Any HVAC Folks in Here? [Re: theguyonthecouch] #1283260
03/02/15 11:36 AM
03/02/15 11:36 AM
Joined: Jan 2015
Posts: 26
NAL
T
theguyonthecouch Offline OP
spike
theguyonthecouch  Offline OP
spike
T
Joined: Jan 2015
Posts: 26
NAL
Well, in case anyone is interested, the HVAC guy just left. Looks like my compressor is going bad. Says it is working, but not well at all. Good news is the part is under warranty...bad news is the labor, etc...isn't. I need to learn to replace compressors! Heh...well, at least I know now!